System Description on sailboat:
- Isolation Transformer 3600VA
- Multiplus 24/300/70
- Shore power 120V (nominal)
- System Power 220V (nominal)
The only load on the transformer is the Multiplus.
We currently are in a location where the lines voltage is running right at the very top of the USA grid specification (127V). Coming out of the transformer we have 272V. This is over the maximum high voltage cutoff for the Multiplus (270V), so it stays in "Inverting" mode.
My understanding is that applying a load on the transformer output will drop the voltage to something like (127*2*1.05)= 267V which is still high, but would allow the Multiplus to make its line connection and charge our batteries and pass through AC power. Unfortunately, without extensive rewiring there is no way to apply a non-voltage sensitive load to the transformer.
Is there any other way to make this connection work? I have reviewed previous posts on similar issues, and it seems the answer is "no," but maybe something specific to my situation is possible? It frustrating to have to run the generator while shore power is available, but just 1 or 2 Volts too high (but still within local grid power specification!)
I appreciate that the usual issue with marina shore power is LOW voltage and this might be the reason for the 5% voltage boost out of the isolation transformer, but this is not the first time we have had this issue and the high voltage problem has been much more often the issue for us.