Hi
On the MPPT RS450, can the DC input be hocked up in series? If you have a string with 8 and 4 modules, 12 are too high voltage. But if you can but MPPT1 in series with MPPT2 it would work. Does someone know if that is possible?
thx
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi
On the MPPT RS450, can the DC input be hocked up in series? If you have a string with 8 and 4 modules, 12 are too high voltage. But if you can but MPPT1 in series with MPPT2 it would work. Does someone know if that is possible?
thx
Hi, sorry but, same as with all our other mppt models, that is not possible