Specifically, can I stack two 24V chargers in a 48V bank made from eight 6V batteries in series? There would need to be DC ground isolation from both the AC line and safety ground.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Looks like no one here knows.
As it's not mentioned in the manual, either assume not isolated, or check with a distributor.
Hi @DDW , apologies that this took me a while! Here is the answer:
Stacking chargers in a battery bank made by multiple 6V (or 12V) batteries connected in series is possible.
Note that there are a few important things to take into account:
1) The nominal voltage of the resulting battery bank is limited to a 48V. Doing this on a higher voltage battery bank will damage the charger.
2) Each of the chargers must have its + and - connected to a battery. This will help keep the batteries balanced, but is also necessary since the chargers may or will fail when only the first charger has its minus and the last charger has its positive wire connected.
In other words: stacking multiple chargers in series to create a higher voltage charger/power supply without adding each individual charger to a battery is not allowed.
I hope above is clear. (In due time) we'll be adding this including a schematic picture to the manual. Thanks for asking!