Similarly, the two + terminals might also be tied together (as long as its either-or but not both)?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Similarly, the two + terminals might also be tied together (as long as its either-or but not both)?
Not sure what you mean. Maybe sketch the proposed wiring diagram.
It's OK to connect the outputs in parallel to increase current to a battery bank for example, wiring the outputs of two 10A units would make a 20A charger. Assuming both have same settings.