Functional purpose of voltage sense wires?

Can someone shed some light on the intended functional purpose of the Voltage Sense wires on a Multi/Quattro?

Are you using it? If so, how/why?


The manual says loosely that it's "to make up for voltage losses across the wires".

With the volt sense wires connected or not connected, under minimal load or loads in excess of 100A, I've never seen any change in the reported voltage by the system.

This was true even before my installation of a BMV (with the lithium batts) and still so now, since SOC and voltage readings (I assume) are now coming exclusively from the BMV.

The voltage reported (by the BMV) is within .01 V of the voltage reported by the BMS on the batteries with minimal load, and within the expected 2-3% difference under heavy loads.

I'm using 2/0 (70ish mm cross section) wires and runs are around 10-13 ft to the batteries. The BMV is 5-7 ft to the shunt. 24V lithium system.

The lead-acid system prior was considerably sloppier, although still using 2/0 cable, and I still recall no differences.

BMV Battery MonitorvoltageVE.Bus
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ben avatar image ben ♦ commented ·

They're important in my system, because there is definitely voltage sag under load.

Where are you looking when you describe seeing "reported voltage"? Victron systems report different voltages in different places, and it can also change depending on what options you elected in the software.

The quickest way to determine if you have any sag (and I suspect you probably do, at 100A with 12ft of 2/0 and presumably at least one fuse and contactor) is to take your multimeter and probe the batteries and then the DC input terminals of the inverter directly. Do so while the system is under a continuous, heavy load, and let us know what you find.


0 Likes 0 ·
geomz avatar image geomz ben ♦ commented ·

Thanks @ben.

I'm comparing the voltages as reported by the BMS (I figure it's the closest point to the batteries and spot on with a multimeter) with the voltage reported by the BMV and by the inverter. For the inverter, I'm looking at the DC voltage for the inverter itself in CCGX, under its own entry there.

I do have some sag, it's the expected 2-3% under heavy load.

But nowhere is that reflected/changed on my displayed numbers (BMV, CCGX, alert triggers, etc) any differently with or without the V sense cables.

Perhaps it's more of an issue with lead as there's heavy voltage sag with them under load and not as much with lithium? But, that shouldn't really be an issue, because that sag is internal to the batteries themselves, and not as much because of the wiring/fuses/etc.

0 Likes 0 ·
ben avatar image ben ♦ geomz commented ·

The sense cables are to eliminate the drop due to interconnect, which of course varies a good bit depending on your circuit.

This drop is actually more important when using voltage-based charging strategies on a lithium pack, since lithium batteries exhibit such small voltage differences to begin with.

When the sense cables aren't hooked up, the inverter will report the voltage it measures on the main power cables. As soon as the sense wires are connected, it will instead show the new voltage. (This is the inverter input voltage reported under that module in the CCGX UI.)

You should be able to see it change, unless you have superconducting power cables or something.

I'm just trying to help you figure out why you don't see it, first. Whether it matters or not is a separate question and will depend on the rest of your system design and your personal preference.

Can you just put your meter directly on your DC input terminals on your inverter, and then put your meter on that end of your Vsense cables, and see what it says for each?

0 Likes 0 ·
geomz avatar image geomz ben ♦ commented ·

I'll try to do that sometime this week and see if there's any difference. I ran similar testing when I installed the system. But I'll try it again with more meticulous/controlled testing procedures. I guess in the long term it doesn't really matter, as I have already run the cables and attached them. I just saw no difference and wondered if I'd just wasted a bunch of time for no reason :D

0 Likes 0 ·
geomz avatar image geomz geomz commented ·

And LOL, re: superconducting cables.

I got a set of Victron's new superconductors.

They're hush hush, and keeping the nitrogen cooled conduit plasma flow stable is a bitch, but boy it's worth it ;)

0 Likes 0 ·
ben avatar image ben ♦ geomz commented ·

If your BMS has full charge authority and you trust it, then whether the inverter has the very best voltage data is not so important... it won't be doing much other than possibly triggering a LV shutdown or something.

Alternatively, if your BMV has good voltage data, you can now turn on Shared Voltage Sense, and your CCGX will "overwrite" the inverter's internal voltage reading with the one from the BMV via software. In a roundabout way, this may achieve the equivalent of a Vsense pair.

But if neither of those are true, Vsense can be very useful or even critical.

0 Likes 0 ·
Allan Yates avatar image Allan Yates ben ♦ commented ·

A quick calculation with values predicts a 0.25V drop across the length of the cable. Thus 12V at the battery charger will be 11.75V at the battery. With the voltage sense wires, the charger will raise its output voltage to 12.25V so as to get 12V at the battery. (Using a 12V target voltage as an example)

0 Likes 0 ·
6 Answers
Paul B avatar image
Paul B answered ·

Keep in mind that the volatge sense also increases the charge voltage by the volt drop so that the batteries get the corrected volatge for charging

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

benl avatar image
benl answered ·

This is 4-wire sensing aka Kelvin sensing, a basic electrical measurement technique.

https://en.wikipedia.org/wiki/Four-terminal_sensing

Whether it makes a practical difference in your setup is dependant on cable size and current load, as others have noted. Unless you've massively over-sized the cable it would be a worthwhile thing and provide improved regulation.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rjoustra avatar image
rjoustra answered ·

Do you have to enable voltage sense somewhere. I am still seeing the inverter voltage reading on my cerbo not the voltage sense wires I installed based on reading I am taking at the inverter and at the batteries under load.. I installed them on my L2 inverter in a split phase system would I need to install them for both or move them to the L1 inverter?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

neeyee avatar image
neeyee answered ·

I have this same scenario where I have attached the voltage sense cables to the indicated + and - terminals and the voltage reported by the Multiplus did not change or improve.

This is a standalone install of Multiplus 5kva with 400Ah of batteries - there is a delta of 1.2v between battery voltage reported on Ve Configure and measured by multimeter at the inverter and battery terminals. Measuring at the inverter terminals vs battery terminals using a multimeter shows a 0.1v difference so clearly there is some sort of internal calibration issue with the Multiplus

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ludo avatar image
ludo answered ·

I have exactly the same problem on my 12/3000 unit, seems to be "systematic".


pls. Victron, do something for us ;)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ludo avatar image
ludo answered ·

OK, so i now checked some things, changed battery from "individual" to LiOn, set charge current to 120A and send the settings to the MultiPlus.

BUT, this time (for the first time) i didn't send only the modified, but ALL settings.


Now my AC-current limit is working, AND my DC-sense- wiring is working.

Thanks for nothing, Victron.


2 |3000