question

mildred avatar image
mildred asked

Can I chain Multiplus and use Power Assist to have more power ?

I find it hard to get information on how the Multiplus works. I own a Multiplus 48V 5000VA 70A and for a long time I thought that the maximum current draw from the battery was 70A while it seems it's in fact close to 105A (5000/48). I also thought that the maximum output power was 4000W(5000VA) but on the enclosure it's written "AC transfer capacity 100A". Can the Multiplus deliver more than 4000W if it has its AC input providing the needed power to compensate?


My goal is to extend the system because I am frequently overloading it but I cannot extend the battery pack because I don't want to mix different batteries together. I'd prefer to create a second battery pack. Something like in the following schema :

2021-12-27-schema-multiplus.jpeg


The second multiplus having a n AC transfer capacity of 1000A, it is more than enough to transfer the 4000W from the first Multiplus and produce in addition to the second multiplus inverter a total of 8000W.

Will this work?

What can make the second multiplus overload?

cascading inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@mildred

The question of a cascade setup has been asked quite a few times on the forum. It is not really an officially supported setup. There is even a tag for it, and it is discussed alot in threads without the tag.

To be honest I have found that it is easier and safer to split the DB board over the two inverters. The ideal way is a parallel system but with your two separate banks that is not really an option.

Transfer ability is referring to how much can pass through not how much it can produce. 4000W is what it can produce. And they can pass 100A through. But obviously it will overload if grid goes out.

With the current draw from the battery the amps go up as the voltage of the bank drops down so often you will draw more than expected unless the bank is massive. 5000va ÷ 48V is 104Amps so what you are seeing is what I would expect to see when the bank is carrying a full load. Or more if your voltage is sagging lower than that.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
I think the AC in can be parallelled between the two as well. Not as shown in Mildred's diagram.