Link the DC of three Pylon stacks on a three phase Multiplus?

Hello,

Is it vital to link the DC Side of three stacks of 5 Pylon US2000? I guess so, just want to make sure.

It's a three phase system (3 MultiPlus 5000) with 5 Pylon for each inverter.

Thank you for your short answer!


Pylontech3 phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

if its a 3 phase system then all inverters should be connected to ONE battery bank not 3 separate banks.

So yes they should all be linked so you end up with one LARGE bank