I recently installed a 12v/3000 Multiplus. I love the features and I am able to remotely monitor and control from the Cerbo GX I installed. Testing the equalization function today and subsequent searching here I see by pressing the equalization charge from the GX Touch that the current into the battery is limited in equalization to 20% of the max (120 ^ .20 - 24 amps DC. I have a 1000 amp hour battery bank of tubular traction batteries. 24 amps will never push the voltage up high enough to reach equalization voltage. Am I missing anything here with the equalization charge functionality of the unit?
My thought on a workaround is to simply change the charging parameters when I want to do an equalization charge. Setting the absorption voltage at 16v and the absorption time at a fixed 4 hours.
Thanks in advance for any suggestions or input.