stillrv asked

Can the current be limited on the AC2 output of a Multiplus 12/3000 120v?

Hi, in my RV I plan to connect my air conditioner to the AC2 output of my Multiplus because I never want to run the air conditioner with the inverter. But the Multiplus will pass through my 30A service on AC2. My air conditioner circuit is a 20A circuit (12 gauge wire). Is there a way to limit the current on the AC2 output? Is there a fuse that can be changed or a programmable setting?

I'm trying to avoid having to install a sub panel for this one circuit.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

The only limit is the passthrough limit for the whole inverter for the AC2 out connection as its normally only powered when there is incoming power on AC1 in. I would think that you could limit it by using the AC in limit setting but this would also affect AC1 out as well