I have a 12v lithium 340AH battery with 600w of solar connected and 12v loads. I will connect charger to a generator to charge battery when solar is not sufficient. Can I connect the charger with the solar and 12v loads connected?
Cheers
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a 12v lithium 340AH battery with 600w of solar connected and 12v loads. I will connect charger to a generator to charge battery when solar is not sufficient. Can I connect the charger with the solar and 12v loads connected?
Cheers
I am planning exactly the same operation, an old Phoenix Charger as charging support in the generator operation. The Phoenix is not built for LiPos, but for lead batteries. So there are a few things to keep in mind.
However, you should set the charging voltages accordingly on the Phoenix Charger. Here I would leave some reserve up so that the charger cannot fully charge the battery. I would also replace the temperature sensor with a fixed resistor so that no temperature compensation (increase in the end-of-charge voltage) takes place.
You don't want to fill the battery with this charger, you only want to achieve a corresponding SOC when the solar power is weak. The rest can be done by the solar charger with the set LiPo mode.