Internal Fuse pheonix 12/375

I'm looking for clarification on the 2x40amp internal fuses in the Pheonix 12/375. Does having two fuses mean they are effectively triggered at 80amps?

fuses
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Andre du Rand avatar image
Andre du Rand answered ·

Hi Lulu-Venchurro,


There is only 1 x 40A fuse installed in the DC circuit inside this Inverter. This is a thermal fuse which allows the peak discharge current for short periods.

2 |3000