I have a Multiplus 48/5000/70 and a CCGX
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello Boris,
That is not a standard feature in the Generator start/stop function of the GX device.
If there is a generator Controller fitted to the generator this type of setting can be set on this controller. The Controller switches on or off a built in contactor applying or removing all AC loads from the generator allowing the warm up and cool down periods.
If no AC Contactor is fitted, a external contactor can be fitted with a timer circuit to achieve this operation.
Hi @Boris1972,
This feature was recently added - https://www.victronenergy.com/blog/2023/05/31/venus-os-v3-00-generator-start-stop-improvements-ess-peak-shaving/
Additional resources still need to be added for this topic
GX - Generator auto start/stop