boris1972 asked

Is it possible to have a warm up and cool down time when you start and stop a generator automatically via a CCGX.

I have a Multiplus 48/5000/70 and a CCGX

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Andre du Rand avatar image
Andre du Rand answered ·

Hello Boris,

That is not a standard feature in the Generator start/stop function of the GX device.

If there is a generator Controller fitted to the generator this type of setting can be set on this controller. The Controller switches on or off a built in contactor applying or removing all AC loads from the generator allowing the warm up and cool down periods.

If no AC Contactor is fitted, a external contactor can be fitted with a timer circuit to achieve this operation.