Cerbo (Multiplus/Quattro) 3 Wire Generator Connection- how?

Hello everyone.

My generator has a 3-wire stop start connection as follows.

Close wire 1 and wire 2. This has a 12v potential and effectively turns the ignition on.

Then I pulse wire 3 - this starts the genny..

To turn off the genny I cut the connection between wire 1 and wire 2

How does the relay output 1 on the Cerbo work?

Can I close NO-Common (wire 1 and wire 2) on relay 1 and pulse NO-common on relay 2 (wire 2 and wire 3)

Advice sincerely appreciated.


cerbo gxGenerator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

you have to work that out yourself the ccgx device just closes a relay that tells you the gen needs to start. on a cerbo that relay has a NC and a NO relay - so you have to work it out from there


there are many different ways to do this, use timers or buy a generator control interface.