How to set up EasySolar II GX in a configuration which prevents feeding energy back to grid ?

Does the EasySolar II GX feed energy back to the grid by default? If so, how can i prevent that?
otherwise if it doesn't by default, can safely connect it to the grid ?

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

If you use VE Configure with a cable connection you can check, there's a setting for it. I'd guess it's OFF by default, it is on my easysolar, but it's not a II.