Low battery warning settings.

Hi. can anyone confirm that "DC input pre-alarm" setting on multiplus is the level at which VRM triggers a "low battery warning" when configured to do so?

I want to recieve a warning when my batteries reach 50% DoD but not shutdown the inverter..

I use a BVF300 (non victron) board to turn off my loads at 75% DoD but that does not report to the multiplus so I can't get VRM alarms from it.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
bigbadbob76 avatar image
bigbadbob76 answered ·

Thanks Alexandra. :-)

I'd missed the ve bus soc option in alarm rules.

all sorted now.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Bigbadbob76

You dont need a device to do this you can set up an alarm using the vrm itself.

Sertings - alarm rules.....add new alarm rule.

Select the device (ve bus soc, bmv) and set where you want the alarm to start and clear.