I have a customer using a Victron MPPT 250/60 with 3.6kW of PV (and 190Ah 48V Marathon MF/T)
It is exporting from the batteries, so the controller runs at full power for a few hours in the middle of the day in sunny weather.
The controller is isolated from the batteries by a Noark Ex9BP (DC) 63A breaker, but it has tripped a couple of times in the middle of the day. I wouldn't have thought a Victron 60A unit could hold 63A or more for the time needed to trip the breaker?
Aren't they limited to 60A continuous?
From the breakers trip curve, worst case, I get something like:
2.8 hours @ 63A
10s @ 130A
5ms @ 6kA
Is it possible the MPPT circuit control could be switching on and off too quick when doing a retracking under full power, and creating a very high current spike of 6kA for 5ms?
Eg, mosfets have inadequate snubbing? or poor snubbing algorithm in firmware? (if it can respond that fast!) - I'm guessing - any ideas please?