Victron VRM ESS consumption data is not matching meter readings for 3 phase system after firmware update

hello,

i have a Victron installation with 3 quattros 10k, grid connected with PV connected on AC out; i have 2 energy meters one connected on Grid and the other on on PV; Everything was ok for about half year and 2 weeks ago ive decided to upgrade quattros via VRM to v487 around the time ive made the update the VRM started showing bad data for Grid, consumption, PV output.

Im checking daily the data from metters and it shows around x2 more than vrm; as an example yesterday ive consumed 96kw from grid but vrm shows 46; keep in mind this is data from victron metter connected to the system, and this worked ok for months.


thank you

P.

VRMbug report
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi,

This was solved by doing a firmware update of the EM24 meters. Firmware for that is available on Victron Professional.

That fw. update solved what looked like to be continuous rebooting of that meter, or at least its network stack.

And once the GX device had a stable connection, the kWh data was good again.



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @paul.marinas@gmail.com,

The first thing I would check is the configuration of the energy meters on the GX device to make sure that they are still correctly configured there. That changing would result in what you are describing.

It is also possible that doing the firmware update affected the configuration of the ESS assistant, so I'd check to make sure that is also looking correctly configured.

Did you make the firmware update for a particular reason? It is not required to keep your Victron equipment updated to the latest firmware version. Stable systems should be left with their current firmware. It may be advised to revert it back if those don't resolve it.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi @paul.marinas@gmail.com , I'll send you an email.


Two things I noticed that need fixing before looking further into the kWhs are that (1) the connection both your ethernet-connected EM24 energy meters (grid & pv) is not stable. Those meters are all the time being disconnected and then reconnected again. The GX device itself seems to be connected via ethernet (not wifi) and that ethernet connection is stable.


And (2) the CPU load of the GX device is high and/or too high. But lets start with fixing the above. This connection issue increases CPU load a lot.



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paulmarinas avatar image
paulmarinas answered ·

thank you for all your help, this was a very positive experience.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources