Hi, if I enable triggers for more than one parameter (say Vbat1 high/low and Vbat2 high/low ), how will the relay act?Logic AND or logic OR to turn on the relay?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi, if I enable triggers for more than one parameter (say Vbat1 high/low and Vbat2 high/low ), how will the relay act?Logic AND or logic OR to turn on the relay?
Sorry for not giving you a great reply, as this is a general forum and not a victron tech support site so most replys are from individuals who dont work for victron, but we try to help out were we can.
I would just test it by putting amounts in yourself and seeing the results.
I would have to do that if I want to know, its quicker that waiting for a advanced reply from the Techs,
I recently read the documentation carefully and it seems to be specifying that the relay closes if ANY specified condition is met (OR) and then it opens back up if ALL thresholds for opening are met - (AND).
So, if I understand correctly, if you set BMV relay to activate when starter battery goes above 13.5 v and you also set to activate when house battery goes below 70% charge, then if BMV see either condition, it will activate relay.
Then where those same parameters have deactivate thresholds - starter battery < 13.3, house battery >90% charge then both will have to be true to deactivate. AND
I hope I got that right. I need an AND logic for activation, OR logic for deactivation so I plan to experiment with this at some point, trying the "invert" setting to see if this inverts the logic as well.