question

kuucity avatar image
kuucity asked

DVCC error #48

Could the DVCC error #48 damage the battery of cause any issue to the inverter? I have just noticed that the firmware of the inverter is on 200 version and it is connected with a fronius grid tied system. Please advise

Pylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·


@Kuucity

If your system does not meet all the dvcc requirements, it should not be enabled. But if you do have Pylontec it gets forced on.

We do need more detailed information on your system to be able to help further.

Usually we would say update all the components, reprogram and try again. But only try this if you know how to set up with the fronius.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kuucity avatar image kuucity commented ·
@Alexandra, Thank you for your response. I shall get another 400 version of the quattro control PCB as stated in the DVCC manual.
0 Likes 0 ·