question

ziad avatar image
ziad asked

400 A Energy meter to Cerbo GX

Hello

Is there a way to connect high power three phase energy meter to cerbo GX ?

I have a power transfer system of 90 kW, with a PV backup system of 16 kW, and i need to measure energy transfer from Grid, PV and the power transfer system.

Some posts talked about the EM24DINAV53DISX energy meter, but i cant find if it support the transferred power.

Energy Metervictron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Ziad

They are for systems over 63A per phase. The difference in what they measure is based on the cts you pair them with and can accommodate the cables amps etc. These are a usually separate purchase.

They are not like the shunt based ones so the amps dont pass through the meter.

https://www.victronenergy.com/live/energy-meters:start

Q8: I want to use Current Transformers (CTs), is that possible?

Yes. You can buy the CG EM24DINAV53DISX directly from Carlo Gavazzi or one of their distributors. Even though Victron does not stock that type of meter, we do support it in our software. The EM24DINAV53DISX is the solution for three-phase systems that go over 65A per phase.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Energy Meter Selection Guide

Additional resources still need to be added for this topic