Multiplus 24 V 3000 Aux fan wiring

Looking to add blower fan to my 24V 3000. The blower is 12V. Should a 12V power be applied to the relay to have it act as a switch?

relay assistant
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mrhappy avatar image
mrhappy answered ·

Yes, as long as the fan is pulling 4 amps or less (48W). If it is pulling more power, then "the relay" in the multiplus could be used to activate a bigger relay which act as the fan switch.

Edit: I assume you are talking about the primary relay (alarm relay)

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kwalstad55 avatar image kwalstad55 commented ·
Thank you mrhappy, I am looking for advice of which relay to use. I want it to turn on & off with the Multiplus fan. The unit I am going to use is a 130 cfm blower 12V 2.5 amps.
0 Likes 0 ·
mrhappy avatar image mrhappy kwalstad55 commented ·

It should be fine to use the primary relay.

You have to program your unit with VE Configure. Add two "programmable relay" assistants and configure them to activate the primary relay based on the fan. Here is a summary example: