Hello,
I'm currently using 2x MP2 in parallel as an ESS recently I started to do grid balancing and charging batteries at cheaper rate from the grid, naturally since energy is cheaper I'm using more loads in the house as well, I've noticed my grid connection is getting pretty close to the limit when batteries are charging and using the shower at 72A.
Grid connection is 100A but I have my own fuse of 80A (so I don't blow the suppliers fuse and for electrical regulations)
Would there be a configuration/assistant, to throttle back the charging so not to exceed the grid connection? At this moment it's unlikely to blow the fuse but I have the third MP2 on the wall, haven't connected it yet, once I connect it chances are I'll blow the fuse.
The ideal solution would be a setting similar to Feed in limitation in ESS assistant.
Thanks in advance.
George