dave-t-1 avatar image
dave-t-1 asked

skylla IP65 DC fault current

I am looking for a reference for the available DC fault current and duration for the Skylla IP65. It isn't stated in the datasheet or installation manual. Possibly it is stated in another document? Note: fault current from the battteries is easily calculated and is a different aspect

documentation
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The charger wouldn't produce much moe than its rated output if the failure mode was a loss of regulation which is most unlikely, besides there are most probably protections inside for this type of falure. In a very unfortunate circumstance, a short circuit within is a more likely failure mode in which case the batteries will supply the fault current.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.